Is there a document which describes the power requirements of a NAP 250 (non DR with EU PSU) during switch-on?
During normal operation my two 250s behave very benignly, only when I switch them on too quickly one after the other, they occasionally trigger a fuse in my home. The fuse is specified as 16A, so I assume the switch-on current must be somewhere above 8A?
So assuming that the fuse 16A is of type B (3x-5x) and that one amp alone does not trigger it but two can, one should conclude that the inrush current for a single amp is between 24A and 40A?
As you say it occasionally happens when you switch both on too quickly, just stagger the switch on of the two 250 amps to limit inrush current and the nuisance trip.
A Type C breaker will certainly help here. Naim recommend that I put my HiFi on a 32Amp Type C breaker (NDX/282/200 at the time) although if you are outside the UK you should seek local advice on this.
Hi JochenF, I assume you are living in mainland Europe, where power circuits are radial & protected with a 16 amp fuse or circuit breaker.
This is different to UK with ring circuits protected with 32 amp circuit breaker. So you need not follow any UK 32 amp suggestions with the various type rated circuit breakers.
Maybe better if you ask an electrician with full knowledge of your countries regulations for help, be sure you know if you do have fuse protection or circuit breaker, and explain the problem is the fuse/circuit breaker in your house does not support “the transformer in-rush current at power up”
Thanks for all the suggestions. Yes, I live in mainland Europe. For clarification it’s indeed a circuit breaker not a fuse, up until now I didn’t know the difference.
I don’t own the electrical installation here, so I will not be able to change the circuit breaker. I need to be careful when powering on, that’s OK. I just wanted to make sure that a triggered circuit breaker is indeed expectable behaviour and that the NAPs are fine nevertheless.